Upstairs weight limits?

huggers

Site Supporter
Sep 22, 2016
1,443
1,220
113
West Dorset
This may well be a stupid question. So guys, I currently have my gym/weights in my upstairs games room because lockdown. There's probably north of 200kg in there. There's also a load of other sh1t including an arcade cab which I built up there which weighs a tonne. In the not to distant future I plan on sticking a couple of pins in there. It might only be one pin if I buy NIB in which case no drama. Just wondering though if it's two or three does weight in an upstairs room become an issue. I should say as well that before lockdown and definitely after lockdown that room gets busy with my cronies larking about, so could be 6 or 7 of us in there at times. So yeah, anyone know if I need to be concerned with weight??
 
  • Love
Reactions: Hullshark

M4carp

Site Supporter
Jan 12, 2019
1,788
1,474
113
Pembrokeshire
Alias
David
That’s the reason I moved my room to the garage, rooms upstairs in my house spans 18’ across, I know it had huge joists fitted as my wife’s uncle put them there when he converted it as it was a school. You could feel the room floor move if you jumped up and down with all the machines in and people.
Wife made me move to the garage where I built a big room😂

I guess it depends on the span/joist size, concrete structure would be best but most houses don’t have that. My brother recently had a house built with concrete structure, amazing.
Do the bounce test to see if there is any flexing.
 
  • Like
Reactions: huggers

Markjduk

Site Supporter
Jun 19, 2020
53
21
8
Peterborough
Alias
MartyMcFly
I built a gym upstairs in our house and asked the same question of an architect he said if you take the sq ft of the room and multiply it by 20 this is a reasonable guide as to how much weight it can hold safely. So if you room is 10ft x 10ft - 100 sq ft then this can safely hold 2000KG.
 
OP
huggers

huggers

Site Supporter
Sep 22, 2016
1,443
1,220
113
West Dorset
Thanks guys, very useful. The house is 1930's and very well built so that should play in my favour.
 

M4carp

Site Supporter
Jan 12, 2019
1,788
1,474
113
Pembrokeshire
Alias
David
Also relies on the timbers not being rotten, 1930’s house might be worth checking but should be ok. I recently renovated a Victorian house that I own where you could see the floor sloping upstairs and the ceiling below was a bit of a slope. Joists were rotten in wall and had to be jacked up and repaired. Previous owners just worked around the slope!
 

Sako-TRG

Site Supporter
Aug 3, 2018
912
588
93
DG126TW
If in doubt seek a professional but think on it like this:-
If 10 people walked in your upstairs room who weighed 13 stone, would you worry about the floor collapsing? That’s 825 kilo... if another 10 walked in I’m sure you would still feel comfortable....
You’ll be surprised how strong a floor is as long as in good condition.
 
Last edited:
OP
huggers

huggers

Site Supporter
Sep 22, 2016
1,443
1,220
113
West Dorset
Oh a bit of maths/science I like it.
10 ft x 10 ft is 3m x 3m = 9m2
Someone mentioned 2.5kN/m2 as an acceptable load
So that 22.5 kN over the 9m2
1kN = 100kg (Well nearly)
So that 2250 kg.
Quite close to what that architect said.
Okay so let's do some maths. Let's say 6 people weighing roughly 90kg a pop. One or two might be carrying a bit of extra timber but that'll do for now. That's 540kg. My arcade cab must be 100kg. 2 pins at say 150kg each. We're looking at just under 1000kg when the room is full of drunkards. Add in some other odds and ends and my weights and still way under. Plus the room is more like 14ft by 11ft. Think I'm okay, certainly for two pins.
 
OP
huggers

huggers

Site Supporter
Sep 22, 2016
1,443
1,220
113
West Dorset
^^^^^^^ if your floor is in good condition ^^^^^^^
Being 1930s..
Yeah it's pretty good I would say. We fully renovated it when we moved in and a new steel was put directly under one of this rooms walls to make way for open plan kitchen dining type stuff downstairs
 
  • Like
Reactions: Sako-TRG

russdx1

Site Supporter
Jul 7, 2018
371
235
43
Bristol
Got 2 pins upstairs in one room with a fruity on other side of the room, it’s not caved in yet :D

Keep them on the side the beams go into the wall and you prob be fine.
 

cr5000462

Site Supporter
Apr 25, 2020
292
65
28
Wrexham
just speak with a structural engineer, tell them the room size, how much weight you plan on putting in it, the walls below it, and what's already above it.
they will do a floor joist calculation to suit the load, check your joists are the same as what they have given you, and then away you go. explain that its not for building regs etc and they wont have to produce a certificate or anything like that,

ive just had done very similar when I built my extension, ended up costing £130, but I had a few steel beam calcs in that price too not just the floor joists.
 

BigIan

Site Supporter
Jul 21, 2011
3,412
1,595
113
Belfast, Northern Ireland
Alias
ZIG
Not a lot of pins as heavy as 150kg most are 120 or under. JJP and a few others are up there though.

A bed with a couple of people in it and a wardrobe and other bedroom pruck is going to be the weight of 3 or 4 pins
 

Mfresh

Site Supporter
Oct 7, 2012
1,500
1,467
113
Bucks, Paul Rubens
www.pavlovpinball.com
Alias
Mr Sinister
Make sure all the stairs are in good nick before you carry the pins up. One rotten step while you are lifting the pin with all your weight plus most of a pin on one foot and ... well you get the idea.
 

J85M

Registered
Feb 24, 2017
301
181
43
UK
Call a local structural engineer and just ask the question bet you find more than one that will throw up an approx answer, why guess when you can find out from an expert in a minute or two phone call.
 

domlouis

Beta Tester
May 28, 2014
1,345
732
113
Derby
So these calculations are not that difficult. I have attached a screenshot that explains how I would work out the floor deflections. The results depend on how well the joists are built into the supporting walls (simply supported from fully built in). Please note that i have never worked in the house building industry, so take what i am giving you with a pinch of salt. I have, for example, had to play Google Bingo for some of the input data. And i don't know what acceptable floor deflection the building industry works to. So i would still recommend talking to a structural engineer, but at least from a position of knowledge.
 